t.mathew
(@t-mathewarcinfo-com)
Posts: 64
Estimable Member
Topic starter
 

Hello,

In a project we are using Solar inverters with the attached Modbus RTU addresses. This inverter is connected to a Data logger which act as a protocol converter from modbus rtu to modbus tcp. I used port 503 as per the spec of datalogger. Please let me know how to create a frame for the following modbus addresses: 300, 301, 507,1003 and 1070. Because once I link address with a variable, Equipment out of service error is showing. And also do we need to open port from windows 10?

Thank you

Tijo

 
Posted : 17/05/2018 12:12 pm
n.kunzer
(@n-kunzerarcinfo-com)
Posts: 1236
Member Moderator
 

Hi Tijo,

When you are in that situation the best is to try first with a third party Modbus Master like Modscan32

Nico

 
Posted : 17/05/2018 3:22 pm
ED
 ED
(@e-duvalarcinfo-com)
Posts: 138
Estimable Member
 

Hi Tijo

You need to configure Word I/O type frame.
First try with a single frame of limited starting address 300 and requesting only 2 words.
According to the documement you need to check the equipment type you will select.
It is either
Modbus Dec or JBUS Dec.
I would test first Jbus with frame address 300 and then Modbus with frame address 300.

Check the complementary status word on youor frame for error code. No need to click on the ... button

If you get error code 1 or 2 (then you need to change the equipment type from Modbus to Jbus.
If you get error code 102 then you have a communication problem with your device and you need to sort that out first before change the frame configuration.

I hope this help

Best regards,

Manu

 
Posted : 18/05/2018 6:49 pm
t.mathew
(@t-mathewarcinfo-com)
Posts: 64
Estimable Member
Topic starter
 

Hi,

@Nico: I tried with Modscan32 it shows the error Tcp/IP connection terminated.

@Manu: I followed your steps in configuration Node shows an error 701 and frame shows 2045 once it link to a variable.

4143=591 2018 05 2016 10 37 PcVue Mainwindow ARCInformatique
4143=592 2018 05 2016 11 17 Framestatusword

What should we do?

 
Posted : 21/05/2018 1:36 pm
n.kunzer
(@n-kunzerarcinfo-com)
Posts: 1236
Member Moderator
 

That's the point, if it doesn't work with Modscan no way it works with PcVue.

So, fix your issue with Modscan first....

Nico

 
Posted : 21/05/2018 2:01 pm
n.kunzer
(@n-kunzerarcinfo-com)
Posts: 1236
Member Moderator
 

I advise you contact the device manufacturer support first. Once fixed with them with Modscan then you can switch to PcVue.

Nico

 
Posted : 21/05/2018 2:02 pm
ED
 ED
(@e-duvalarcinfo-com)
Posts: 138
Estimable Member
 

Hi Tijo

regarding the test in PcVue as I told you I need the supplementary status word.
So don't click on the "...' button.
Under the 2045 you must have another code displayed . That is the important one. And unfortunatly we cannot see it in you frist screenshot
This code give you the error you have for the specify protocole you selected.

And the code should be explain in the help for the driver.
102 : You cannot connect to the PLC. Check ping
2: you request too many data
1: you request the wrong type of data.

 
Posted : 22/05/2018 11:11 am
t.mathew
(@t-mathewarcinfo-com)
Posts: 64
Estimable Member
Topic starter
 

Hello Nico,Hello Manu,

Problem was from the device side. Solved. Now Connection is good. But I got some error like below for some registers in real data type

4154=594 2018 05 2315 14 31 PcVue D3Solar 23 05 18

In the same equipment for some other registers in real data type, it is working good. Is it is a problem from equipment side?

4154=595 2018 05 2315 37 44 PcVue D3Solar 23 05 18
 
Posted : 23/05/2018 7:49 pm
ED
 ED
(@e-duvalarcinfo-com)
Posts: 138
Estimable Member
 

Hi Tijo

Your frame "301to307" display the error code 2. That is invalid data. You must be asking too many data for this frame.

  • What is the configuration of this specific frame?
  • Starting address number of data and type of data?

If you selected Real type frame then the starting address should be 301 and the number of data (ie number of float) should be 4 and not 8.
Please check and send us the frame configuration that causes the complementary status word error 2.

 
Posted : 23/05/2018 8:11 pm
e.mahaut
(@e-mahautarcinfo-com)
Posts: 270
Member Moderator
 

Hi Tijo,

The 702 code means you have configured a message time out in the node.
While beginning tests, it is strongly recommended not to change the default values.

4156=596 NodeMessageTimeOut

Here is where you can find the meaning of the status 0002

4156=597 StatusModbusIP

Edouard

 
Posted : 23/05/2018 8:41 pm
e.mahaut
(@e-mahautarcinfo-com)
Posts: 270
Member Moderator
 

Tijo,

Could you either copy / paste the content of your .CComm.dat file or give us screenshots of:
- Node Inverter04
- Frame 301to307
- Frame 1090

BR
Edouard

 
Posted : 23/05/2018 9:19 pm
t.mathew
(@t-mathewarcinfo-com)
Posts: 64
Estimable Member
Topic starter
 

Hello all,

@Edouard I changed message time out to 5 sec. Noted your remark and will change accordingly.
The following is copy paste from comm.dat

VERSION,1,0
BOARD,0,1,1,0,0,0,0,,,0,0,""
NETWORK,0,0,Build08,263,,0,0,NO,0,0,0,5,0,1,0,0,,,0#0#0#0#0,,,0,0,"",0,0,3,,,1
EQT,0,0,0,Inverter04,1,MODBUS_DEC,4,0,5,0,0,5,0,1,0,,0,,90#0#0#1#503#0#0#10#0#0#0#0#0,0,,,0,0,"",0
FRAME,0,0,0,0,301to307,3,16,4,R,300,Real I LMsb ,8,0,0,5,0,0,0#0#0#0#0,0,1,1,,,0,0,""
FRAME,0,0,0,1,1050to1054,2,10,5,R,1049,Word I ,2,0,0,5,0,0,0#0#0#0#0,0,2,1,,,0,0,""
FRAME,0,0,0,2,1070to1080,3,80,20,R,1089,Real I LMsb ,8,0,0,1,0,0,0#0#0#0#0,0,3,1,,,0,0,""
FRAME,0,0,0,3,1090,4,24,6,R,1069,DWord I MLsb ,14,0,0,1,0,0,0#0#0#0#0,0,4,1,,,0,0,""

One mistake, I mean to say Frame 1070to1080 instead of Frame 1090 before. I got error only in Frame 301to307.

Initially I created each frame for each registers (for real, word, Dword with number of data as 2,1,2 respectively). It takes long time so as a test i tried following but it worked good expect Frame 301to307.
What I have done is, I gave total number of registers comes adjacently with same date type as the number of data. Then mapped to each tag.

4158=599 2018 05 2409 32 53 PcVue ARCInformatique
4158=598 2018 05 2409 19 09 PcVue ApplicationExplorer D3 solarproject

I dont know its a good method because inverter are not fully operational for verifying the data are good, expecting your remarks.

Screenshots

4158=600 2018 05 2409 32 53 PcVue ARCInformatique
4158=601 2018 05 2409 45 26 PcVue D3Solar 24 05 18
4158=602 2018 05 2409 45 47 PcVue D3Solar 24 05 18
4158=603 2018 05 2409 46 17 PcVue D3Solar 24 05 18

Thank you

Tijo

 
Posted : 24/05/2018 10:36 am
ED
 ED
(@e-duvalarcinfo-com)
Posts: 138
Estimable Member
 

Hi Tijo

You must set the Message time out of your device to 0 and keep the Node time out to 5s.
The message time out as Edouard pointed out is to have a silence between to request so it impact the performance.

Regarding your frame I know what is wrong.
For the range between 0180 and 516 you must select Real I/O and not Real I (or Word I/O if you want to get integer value)
In the doc this range is under the title Holding Register
and the range 1000... is under Input Register.
Please check article KB441 for more detail about the function to use and the type of data to select.

Best regards,

Emmanuel

 
Posted : 24/05/2018 11:46 am
ED
 ED
(@e-duvalarcinfo-com)
Posts: 138
Estimable Member
 

Let us know if it works now.
Thanks

Manu

 
Posted : 25/05/2018 11:08 am
t.mathew
(@t-mathewarcinfo-com)
Posts: 64
Estimable Member
Topic starter
 

Thanks Manu,
The site is busy with some other works, so we may go after 3 or 4 days. I will let you know once I check it.

Tijo

 
Posted : 25/05/2018 11:21 am