Hi,
I encountered recently an issue with Alert that I would like to share with you.
Context: Some tags are declared in Alert and NOT in PcVue. Tags are using whatever OPC or DDE channels.
Effect: Alert is periodically disconnecting the OPC/DDE connection and reconnects.
In Log Filesopcsrv.log we can see this sequences indefinitely
2017/04/14,23:50:19.402,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,Connection of a new client '2'... 2017/04/14,23:50:19.402,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,...Client '2' is connected... 2017/04/14,23:50:19.402,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,Client '2' is setting its name... 2017/04/14,23:50:19.402,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,...Client '2' name set as 'Micromedia' 2017/04/14,23:51:37.218,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,Client '2' is deconnecting... 2017/04/14,23:51:37.218,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,...Client '2' is deconnected 2017/04/14,23:51:39.280,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,Connection of a new client '3'... 2017/04/14,23:51:39.280,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,...Client '3' is connected... 2017/04/14,23:51:39.280,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,Client '3' is setting its name... 2017/04/14,23:51:39.280,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,...Client '3' name set as 'Micromedia' 2017/04/14,23:54:53.866,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,Client '3' is deconnecting... 2017/04/14,23:54:53.866,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,...Client '3' is deconnected 2017/04/14,23:54:53.928,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,Connection of a new client '4'... 2017/04/14,23:54:53.928,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,...Client '4' is connected... 2017/04/14,23:54:53.928,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,Client '4' is setting its name... 2017/04/14,23:54:53.928,NSNG1201XAP,svc_emrs_sgp,OPCSVR,I,0,0,...Client '4' name set as 'Micromedia'
Nico
Thanks Nico
What are PcVue and Alert versions ?
A very recent one.
But, for sure, even the last one has the same behaviour. Actually it's not a bug, Alert is done like that apparently!
Nico
But why do you have variable in ALert and Not In PcVue ?
These variables in ALert are connected to PcVue ?
Typically the customer has removed some variables from PcVue but forgot removing also in Alert...
Nico
Ok, so Bug coming from PcVue OPC/DDE Server which not accept suscribe for inexistant variable and cut communication with ALert and after Alert restart communication again and again.
Ho, I didnt understand in that way.
In this case => SPR