PcVue and Siemens S7-1500R and ET200SP

2 Posts
2 Users
0 Likes
36 Views
ANSO
 ANSO
(@a-solovevaarcinfo-com)
Posts: 16
Eminent Member
Topic starter
 

Hello all,

1. Can PcVue work with S7-1500R and ET200SP?
I found KB820 for S7-1500 (not redundant version) about CP1543-1. Does R version is also supported in the same way?

2. Is it possible to import the configuration from Step 7 for S7-1500R via Smart Generator?

3. Which protocol should be used in PcVue?
S7-IP-MASTER?
Or IP-ISO-S7 as for S7-1200?

Thank you in advance.

 
Posted : 01/03/2019 11:44 pm
BO
 BO
(@b-olombelarcinfo-com)
Posts: 196
Reputable Member
 

Hello,

1. Yes PcVue should be able to communicate with this PLC. For redundancy, I guess you can use the "Redundancy" option in the "Node" section of "Node Parameter".
2. From 11.2 version, the smart generator contains a TIA Portal import, we let you test it ;-).
3. IP-ISO-S7.

BR

 