Hi,
I am trying to connect TURCK TBEN-L5-PLC-11 PLC Codesys OPC UA server. I am successfully connected to the OPC UA server but the variable mapping list is not as per expected. Major variables are missing in PcVue but available in OPC UA client.
Attaching the images of OPC UA client, PcVue.
Thanks & Rrgards,
Nitesh Dongare
Hi Nitesh,
Difficult to see as it is very small.
By the way, could you show also the result with the other OPC-UA client.
To be complete, please specify the version you are using.
Nico
Hello Nico,
I am using PcVue 15.2.1.
I have attached images of result in Open OPC-UA client.
Thanks & Regards,
Nitesh Dongare
OK, to test OPC-UA you must take the version 16.0 (Main) and not 15.2.x
Nico
Hello,
Our customer (Turk India Automation Pvt. Ltd.) is doing this testing in their lab. Can we share version 16.0(main) with them?
Thanks & Regards,
Nitesh Dongare
Hi Nitesh,
On the sales side, there could be some agreement to set up for 16.0.
On qualification side, some information are needed. You should receive an email soon.