No real experience for me.
How many OPC Clients your customer wants to connect?
Nico
The answer from the customer is about 100.
OK that's quite a lot.
May we know a bit more on the context?
I mean:
- Do these clients are reading only or writing only or read/write?
- What client is it? Is it another HMI or just a communication gateway?
- Why so many?
Another points you must take care in term of limits are:
- How many groups created by Client. Imagine each client creates 10 Groups then we will have 1000 Groups.
- What Period and DeadBand will be requested? Meaning what is the expected dataflow (datachange per second)?
Nico
Sooooorry Nico, I mis-understood the customer's requirement. They will have many OPCServers communicating with PcVue OPC Client. There are around 100 OPC Servers and each server has about 1000 tags.
BRS,
Mark
Hi Mark,
It is much better that way, PcVue as OPC Client.
Usually, even OPC server from famous companies are not connected to so many clients. I would say 5 is really the maximum.
Regarding the customer challenge, how do they test it?
Do they have up to 100 different OPC servers? Or they declare many times the same. It is not comparable at all.
For the first case, congratulations to your customer.
For the second case, the OPC server has to be very reliable.
BR
Edouard
Hi Mark,
I will have soon an answer from development team about the OPC Server limit and I will update this post accordingly.
But, the real important point is the loading of the computer. To evaluate it you must answer these questions:
1. How many PcVue clients to dispatch the data?
2. Is it only OPC data to collect or other data (Modbus, bacnet, etc...)?
3. Does the computer also an Archive Server?
4. What data flow is expected? Meaning: How many datachange per second per OPC Server?
Without these information we can't advise anything.
Nico
Hi Mark
On the docportal, there is a document : PcVue figures and limitations_English
You can find :
OPC DA Client
Maximum recommended number of OPC servers that can be configured : 10
Maximum recommended number of OPC groups that can be configured : 50