I have a requirement in a project where IEC-61850 is massively used.
Customer wants to have an alarm in case of timeout in sending IEC-61850 commands.
Any idea to do it easily without playing with tons of scripting and re-do all animations? 🙂
How I can detect from PcVue a writing timeout in the driver? By parsing TRACE.DAT file? :dry:
Thankyou!!!
Hi Filippo,
If it is a bit you can use the variable Discrepancy behavior.
If it is a register then I think the most easy way is to make your own discrepancy behavior by scada basic
- Call the SB procedure passing the branch + value & discrepancy time in arguments
- Send the control to the value
- Set a cyclic with the period + the variable to check in argument
- When cyclic triggers:
a Kill the cyclic
b Check the value and set and alarm if value is not good
Nico
Ciao Nico!!!
Thanks a lot!! It's a bit and Discrepancy it's perfect! 🙂