Hi,
One of our customer encounters an issue regarding the scheduler.
He created 348 schedule actions (time table only) but when I start a project I can see only 333 schedules in the Action/Scheduler dialog.
Worst, if I save it will save only those 333 meaning we are losing the last 15!!
I retrieved a thread done by Nagen in Yammer. This is his last answwer:
"Nagendran Jayagobal said: The answer from our Developer:
In fact there is almost no limit in memory (1 million since version: 8.10 SP6 - 8.20 SP1 - 9.00).
The HMI of the configurator is limited in 512 but there is no problem if you configure them via the cron.dat."
But here, apparently, we are not in the same case: Total of 348 schedules and, 333 displayed in the dialog. I made a TimeTable animation configuring one of the 15 missing. It's not working meaning the 15 missing are not taken in account.
Does somebody had a similar experience/idea?
Thanks,
Nico
No similar experience/idea.
Which version are you using ?
Yes sorry I forgot to specify its the last 10.0 Update1 :S
Meanwhile you can put it in the Guiness book I think.
Who can manage 333 time table?
Hmmm I think we have many BMS projects having more than this amount!
You should know that in a BACNet or Lonworks controller there is many schedule objects. Each object is one Time Table....
During our last ITM I received a project having more than 1300 lonworks controllers.... (in The Guiness Book by the way 😛 )
As it is not me who has to manage 😛
I just realized that this topic is solved as I made a SPR.
Fix done in 10.0 SP1 Update