IBH Link S7++ with Driver of IP-ISO-S7

4 Posts
3 Users
0 Likes
22 Views
n.kunzer
(@n-kunzerarcinfo-com)
Posts: 1236
Member Moderator
Topic starter
 

Hi guys,
Anybody has an experience using this converter?

PcVue --ISO-IP-S7--> Converter --MPI--> PLC

http://www.ibhsoftec.com/IBH-Link-S7-PP-Eng
http://wiki.ibhsoftec.com/en/IBHLink_S7%2B%2B:IBH_Link_S7%2B%2B_with_CommDTM

 
Posted : 03/09/2013 3:03 pm
ED
 ED
(@e-duvalarcinfo-com)
Posts: 138
Estimable Member
 

Yes it works fine and has been implemented on a couple of occasion.
Be carefull our ISO IP S7 driver does not support routing i.e. the connection need to be done directly onto the PLC CPU. If you use a CP then you will need to buy the IBH OPC server at around 309£ that support the routing (validated on S7 300 but not with S7 400 as foar as I know.

 
Posted : 03/09/2013 10:27 pm
(@m.nau@ypsys.com)
Posts: 0
New Member Guest
 

Yes Nico, It works really fine.

We use it in a lot of plants. In Messier Bugatti, there are using it with PcVue (Hilscher driver in PcVue), you can ask Franck Berruyer.

If you need more technical information, Julien and Jérome (support@ypsys.com) knows this IBH SoftNet perfectly.

 
Posted : 06/09/2013 2:02 pm
n.kunzer
(@n-kunzerarcinfo-com)
Posts: 1236
Member Moderator
Topic starter
 

Thanks guys!

 
Posted : 06/09/2013 2:14 pm