Hello,
is there any limitation about PLC Number with ModBus RTU ?
Thank you
Hi Brice.
There is a knowledge base article available that refers to version 7.00 and older:
https://staging.pcvue.com//wp-content/uploads/kbase/communication_interfaces/Limits.gi f" alt="">
KB102
For newer versions I don't know...
The KB102 article deals with the theoritical number in a CimWay configuration.
Regarding Modbus RTU, the number of PLC on a Modbus RTU network is limited to 255. And actually you need electrical repeater to reach this number.
Usually without repeater on the line the max number is 32.
Thank you !!!