I got a customer who used PcVue 10.0 SP1 to communicate with Siemens 300 using Siemens IP-ISO-S7. And, found that:

1. Send the command (e.g.@CMD) from PcVue side, in the PLC it changed within 1s, it's normal;
2. but, PcVue needs 10 seconds to get the changed status(e.g. @STATUS);

The command and status are in two separate frames, with 1s scan rate, even we changed the scan rate to 100ms for the status frame, nothing changed.

At the moment, i did not receive the CW trace. Do you know there is some settings to improve?

Thx a lot.

 
Posted : 17/04/2013 9:10 am
n.kunzer
(@n-kunzerarcinfo-com)
Posts: 1236
Member Moderator
 

Yes, just wait the CwAudit traces first 😉

 
Posted : 17/04/2013 12:10 pm
(@sq.zheng@pcvue.com.cn)
Posts: 61
Trusted Member Guest
 

Yes, just wait the CwAudit traces first 😉

here are the trace,please check the trace after 13:57.

 
Posted : 18/04/2013 9:17 am
n.kunzer
(@n-kunzerarcinfo-com)
Posts: 1236
Member Moderator
 

may be you can give us your opinion first 😛

 
Posted : 18/04/2013 12:17 pm
(@sq.zheng@pcvue.com.cn)
Posts: 61
Trusted Member Guest
 

may be you can give us your opinion first 😛

Maybe, the frame to read status is too big. 🙁

It's very strange, because normally PcVue reads data faster than write the command.

 
Posted : 18/04/2013 12:44 pm
n.kunzer
(@n-kunzerarcinfo-com)
Posts: 1236
Member Moderator
 

I can see this:

[13:58:09:234][0360] Cmd Dump: [ComObj: ] [Type: ] [Reason: ]

then

[13:58:12:281][0360] Cmd Dump: [ComObj: ] [Type: ] [Reason: ]

meaning we read the data 3s after writing.

And then the READ is
[08000000][13:58:23:031][0360] Cmd Dump: [ComObj: ] [Type: ] [Reason: ]
[08000000][13:58:34:484][0360] Cmd Dump: [ComObj: ] [Type: ] [Reason: ]

Meaning you have a read request every 11s. So I am not surprised that, sometimes, you see the value 10s after a write.

What your customer can try is to activate the mode ReadAfterWrite using the Scada Basic function CIMWAY("READAFTERWRITE"...)
Then it will send a read request everytime after a write request.

 
Posted : 19/04/2013 7:35 am
(@sq.zheng@pcvue.com.cn)
Posts: 61
Trusted Member Guest
 

Thank Nico!

So, I just need to suggest the customer to create a SCADA Program to trigger the ReadAfterWrite function for each frame. And then configure the SCADA Basic in the Stations Startup.?

🙂

 
Posted : 19/04/2013 8:05 am
n.kunzer
(@n-kunzerarcinfo-com)
Posts: 1236
Member Moderator
 

Yes but only the frames that you can write.

By the way, it should be good to investigate why a frame set to 1s polling is really polled every 11s...

 
Posted : 19/04/2013 8:38 am
(@sq.zheng@pcvue.com.cn)
Posts: 61
Trusted Member Guest
 

But what about the command and status are not in the same frame?

For the 10s, I referred to Emmanuel, if i have news, I'll update the ticket.

 
Posted : 19/04/2013 10:58 am
n.kunzer
(@n-kunzerarcinfo-com)
Posts: 1236
Member Moderator
 

Shu Quan, this is normal. The protocol allows you to Read OR Write. So, if you set a control then PcVue just send a Write request.

 
Posted : 19/04/2013 11:11 am
(@sq.zheng@pcvue.com.cn)
Posts: 61
Trusted Member Guest
 

Just to update the ticket:

With Emmanuel's help, the problem is solved.:)

It comes from the "message time out" parameter which the customer set it to 1s.

 
Posted : 26/04/2013 11:25 am
n.kunzer
(@n-kunzerarcinfo-com)
Posts: 1236
Member Moderator
 

Arrrgghh!
The classic mistake!

 
Posted : 29/04/2013 12:34 pm