Does somebody have feedback on Siemens PRU or PX equipement.
I didn't find any information on the internet and customer didn't the communication protocol.
Hello,
Siemens PX could be :
- Px80-N
- PXC100.D
- PXG3.M
That's to say your customer is using BACnet gateway.
For Siemens PRU, I don't know anything, sorry.
Manuel NAU response : On Siemens PX protocols and PRU information was found. -PX: BACnet protocol. Already established in Switzerland. - For PRU (P-Bus protocol) there is a bridge Hardware: PCS: dead link
To complete those informations for PRU PRU seems working with Profibus DP protocol. The P-Bus is the Link between PRU & Remote I/0. So with the hardware PCS (www.persy.nl), you can connect the remote I/O and convert in Modbus RTU but not the PRU. I'm still working on how we can connect the PRU in PcVue. Maybe with an applicom card PCI15000pfb. The customer says the have a CP5611 a2 card form Siemens, to take data from PRU to Unigyr Scada : dead link. But I'm still not sure we can replace this card with an applicom card. If you have information about this, I'm your man. 🙂 FWI : for PXG-80N, a project is done in Geneva called Falaises- Pêcherie.