BACNET configuration/d betwenn twos differents LAN

6 Posts
3 Users
0 Likes
37 Views
(@admin_doc72)
Posts: 493
Member Admin
Topic starter
 

Hello

In this case, what is the needed device ?

1103=152 BACNETARCHI

Standard Ethernet router ?
Spécific bacnet device - BBMD ?
Spécific bacnet device - FDP ?

We talked about it during ISM 2011 (I have looked the ppt file) but it's not very clear in my head

Thanks

Nicolas
Atys-Concept

 
Posted : 03/10/2013 2:15 pm
f.cubattoli
(@f-cubattoliarcinfo-com)
Posts: 167
Reputable Member
 

Hello,

In my hopinion, this slide is not very clear about the architecture that you want to do.

- What is the green line? It's an Ethernet network or a different network type like BACnet MS/TP (serial) or something else (LON...)?

If the green line is an Ethernet network (separated from the one which PcVue server is located due of a different subnet/VLAN or a VPN router in the middle) you need to use the BBMD functionality. This because BACnet is based with Broadcast packet which are blocked by Ethernet routers (don't confuse with BACnet router).

I suggest you this document: http://www.chipkin.com/files/pdf/Bacnet%20For%20Field%20Technicians.pdf
Go to page 8

Hope it help,

Kind Regards

 
Posted : 03/10/2013 3:03 pm
(@admin_doc72)
Posts: 493
Member Admin
Topic starter
 

Thank you

My case is : Ethernet network (separated from the one which PcVue server is located due of a different subnet/VLAN or a VPN router in the middle)
So if I understand I just need to configure BBMD but don't need specific router ?

I will read you document

Best regards

 
Posted : 03/10/2013 3:32 pm
f.cubattoli
(@f-cubattoliarcinfo-com)
Posts: 167
Reputable Member
 

Hello,

Yes, you need BBMD.

If you have network A and network B (separated) you need to:

- configure a device, in network A, for using BBMD (just one it's enough, lot of router and devices support that)
- the same of network B (Our BDS stack can act also as BBMD gateway, so you don't need a real hardware device on that network - PcVue it's enough).

- Allow IP address of BBMD device in network A to be seen from network the one in network B (VPN, NAT...)

Honestly I don't have a real experience on that, so if you plan to use PcVue as BBMD for doing that your comments are welcome to share your experience.

BR

 
Posted : 03/10/2013 3:53 pm
(@sq.zheng@pcvue.com.cn)
Posts: 0
New Member Guest
 

Hello,

I had a doc for the BBMD and FDT from Jerome when I qualified the BACnet long time ago, it explains the both architectures. See attached file for detail.

 
Posted : 08/10/2013 10:07 am
(@admin_doc72)
Posts: 493
Member Admin
Topic starter
 

I will look at this soon. Thanks a lot

 
Posted : 08/10/2013 11:30 am